Forum Title: 6 cct on contactor
looking to put 6 ccts (lighting) on a contactor controlled by a time clock. I'm kinda new, and not sure how to go about it. are there 6 pole contactors?
Category: General Electrical Discussion Post By: Hector B (Blaine, MN), 03/23/2017
Two 3 pole contactors is probably cheaper than a 6 pole, if you could find one. Try GE CR206L20GAZZ

- Marlene Bush (Altamont, TN), 03/25/2017

Check 30-710(4) for the rating of the contactor. Appendix B refers to CSA C22.2 #14, which means nothing to me, but it might allow for a lower rating if the contactor is rated in HP. The rule is that for HID lighting, the rating must be double the ampere load.

- Central Heating & Air Conditioning Co. (Sun City Center, FL), 03/25/2017

ASCO makes lighting contactors with as many poles as you need. A mere 6 poles should be no problem at all.http://www.emersonnetworkpower.com/...LightingContactorsforBranchCircuits.aspx

- Ted Tucker (Valley View, PA), 03/25/2017